I am using a single panel mounted on two pivot hinges instead of a two panel system with a piano hinge.
I have to alter the BlueSea #8498 AC Source Selection Panel. Originally it was supposed to be able to select between (3) power sources which were listed as:
Shore 1 30amp
Shore 2 30amp
Generator 50amp
Plus one transfer ----- 30amp
On the top is the standard to wire this panel. However, in order to select a power source between The Firman 3042 Generator and the 50amp split phase Shore I had to attach the Shore Power to the existing 50amp circuit breaker.
Also, the 6 circuit AC panel located just below it is to be connected to the Shere Power/Generator busbar.
On the right side, the two 30amp circuit breakers now designated as:
Shore 2
Transfer
These will be upgraded to (2) 50amp, 2 pole circuit breakers for:
Victron Multiplus II 12V/24V 3kVA 2x120v for:
400-1200 ah @ 12v battery bank (we have 1000 ah)
DC Fuse 400A & 2x AWG 1/0 to 16 ft & 2x AWG 2/0 if longer
AC Out 75A with 75A AC fuse & AWG 6 cable
Victron Multiplus II 48V 3kVA 2x120v
100-300 ah @ 12v battery bank (we have 275 ah)
DC Fuse 100A
The MultiPlus II inverter/chargers will accept either 120v single phase AC or 120/240 split phase AC. The Shore Power is 50amp 120/240 split phase.
The Firman 3042 provides all of the below:
120v single phase @ 30amp
A separate duplex outlet on the generator 12ovac 20amp
A 12vdc out 8.3 amp
A USB outlet providing 5vdc @ 2.1amp
The (2) removable black panel covers on the left protect the AC wiring and connections for both the altered AC Source Panel and the 6 Position AC circuit breaker panel. Below them is an (8) position AC terminal strip with a black cover. All the AC breakers will be wired to the terminal strip sop that the final connection to the AC appliances, etc. need only to be connected to the terminal strip, not the breakers.
In the center is an exposed 12v dc dual minibus that provides a 12v dc connection to all of the LED lights in both the as and dc electrical panels.
Just to the right, on the bottom, is a similar (8) position Dc terminal strip with a black protective cover to be installed in the same fashion.
Above that is the rear of the (8) position 12v dc circuit breaker panel that replaces the original fuse block. are )2) Victron BMV-712 Smart Battery Monitors, one designated for 12v and the other 48v. The only electrical connection is a long RS-45 cable to the corresponding shunts located at the respective battery banks.
These meters have bluetooth, so they can be be viewed and controlled by cell phones, iPads or computers.