Larry Davick
>
> I replaced the coil. Moved the fuel pump and it still did not run for 30 minute when pushed back. I was surprised that the generator started right up even with the fuel pump mounted on the RV frame.
>
> Sick of playing with this generator. Something is heat sensitive. I have two condenser that I can replace. That will be all I could think of.
>
> Well I started to replace the condenser at the points. Guess what it had come lose at the point connection. I tightened the connection. Started it up closed it up and it ran for 30 minutes. It was late so I shut it down and will run it more tomorrow.
>
> Art
>>
>> Art,
>>
>> There is no need to relocate the fuel pump, there are hundreds of Onans that run just fine with the fuel pump where it is.
>>
>> RE: "My coils ohm out right so they should be ok."
>>
>> Not necessarily, the Onan on Double Trouble would run for an hour or so then it would quit. If I opened the door and let it cool down it would run when it got cooler; I'd close the door and it would run for an hour or so and then quit again.
>>
>> I installed a new coil and that fixed the problem.
>>
>> Regards,
>> Rob M.
>> The Pedantic Mechanic
>> Sydney, Australia
>> AUS '75 Avion - The Blue Streak TZE365V100428
>> USA '75 Avion - Double Trouble TZE365V100426
>> USA '77 Kingsley - TZE 267V100808
>>
>>
>> -----Original Message-----
>> From: Gmclist [mailto:gmclist-bounces] On Behalf Of amansfield1104
>> Sent: Tuesday, May 29, 2018 3:58 PM
>> To: gmclist
>> Subject: Re: [GMCnet] Generator ?
>>
>> Thanks everyone. The fuel pump has been replace by one that mounts to the same location as the original generator. I’m going to move that pump under the RV to keep it cooler. In the process I will replace the fuel line under the generator.
>>
>> I ordered new points and condensers for the generator just in case that's the problem. My coils ohm out right so they should be ok.
>>
>> This morning the generator cranked right up. Weather not to good right now so I can not work on it.
>>
>> Art
>>>
>>> Check the fuel lines anyway, heat will can cause an vapor lock or you have
>>> a line that has a crack or hole.
>>>
>>>
>>> J.R. Wright
>>> GMC Great Laker
>>> GMC Eastern States
>>> GMCMHI
>>> TZE Zone Restorations
>>> 78 Buskirk Custom 30' Stretch
>>> 75 Avion (Under going Frame up Restoration)
>>>
>>>
>>> On Tue, May 29, 2018 at 3:08 PM, amansfield1104 <
>>>
>>>> The generator ran for a while when pushed back. The temperature went from
>>>> 110 deg F to 160 deg F. I do not think it is a pinch fuel line. I think
>>>> it is temperature related.
>>>>
>>>> Art
>>>>>
>>>>>
>>>>>> I got it started once but it was running every rough. Earlier today I
>>>> had it running and handling both AC unite. Than I push it back in and it
>>>> ran for a while then quit. Since then it has not run.
>>>>>
>>>>> If it ran for a bit after you pushed it back in then it most likely
>>>> explanation is that the fuel line got pinched.
>>>>>
>>>>> OTOH if it did not run at all after pushing back in then I’d go after
>>>> electrical. I think it would be quite an unlikely coincidence that your
>>>> {points,coil,control board - pick one} failed at the exact moment you
>>>> pushed it back in.
>>>>>
>>>>> Before fiddling with ignition I would suggest confirming whether or not
>>>> you have a fuel delivery problem by the simple test of taking the nut out
>>>> of the bottom of the carb bowl and seeing if fuel drains out. If the bowl
>>>> is dry then you have a fuel delivery problem. Rule that out before
>>>> disturbing other systems.
>>>>>
>>>>> —Jim
>>>>>
>>>>> Jim Miller
>>>>> 1977 Eleganza
>>>>> 1977 Royale
>>>>> Hamilton, OH
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> _______________________________________________
>>>>> GMCnet mailing list
>>>>> Unsubscribe or Change List Options:
>>>>>
http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org
>>>>
>>>>
>>>> _______________________________________________
>>>> GMCnet mailing list
>>>> Unsubscribe or Change List Options:
>>>>
http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org
>>>>
>>> _______________________________________________
>>> GMCnet mailing list
>>> Unsubscribe or Change List Options:
>>>
http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org
>>
>>
>> _______________________________________________
>> GMCnet mailing list
>> Unsubscribe or Change List Options:
>>
http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org
>>
>>
>> _______________________________________________
>> GMCnet mailing list
>> Unsubscribe or Change List Options:
>>
http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org
>
>
> _______________________________________________
> GMCnet mailing list
> Unsubscribe or Change List Options:
>
http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org