Hi All Friends,

I know enough about AC systems to occasionally get in trouble.
And I've read and reread the thread about the change to HC-22a, a while back on the forum.
The rooftop Duotherm unit starts and runs good, cools about a 5 to 6 maybe a 7 on a scale of 10 (it's cool not cold outlet air ). I haven't found
Doracool HC-22a in small cans size (30 lbs. equivalent size only).
My question.
Since Duracool HC-12a (I have on hand) works with any oil and I'd be replacing the freon completely,
can HC-12a work (the same or better) in a R22 system?
Thanks you, for the wisdom and advice.

--
”When we avoid the mistakes we might have made, we sometimes make the mistakes that we might have avoided.”

Adrien & Jenny Genesoto
75 Glenbrook 26-3
Yuba City,Ca. Text 530-nine-3-three-3-nine-nine-6
 
> Hi All Friends,
> I know enough about AC systems to occasionally get in trouble.
> And I've read and reread the thread about the change to HC-22a, a while back on the forum.
> The rooftop Duotherm unit starts and runs good, cools about a 5 to 6 maybe a 7 on a scale of 10 (it's cool not cold outlet air ). I haven't found
> Doracool HC-22a in small cans size (30 lbs. equivalent size only).
> My question.
> Since Duracool HC-12a (I have on hand) works with any oil and I'd be replacing the freon completely,
> can HC-12a work (the same or better) in a R22 system?
> Thanks you, for the wisdom and advice.
https://www.amazon.com/Duracool-22A-Refrigerant-Recharge-Kit/product-reviews/B0155NDZ8A
--
73 23' Sequoia 4 Sale
73 23' CanyonLands Parts Unit 4 Sale
Upper Alabama
"Highest price does not guarantee highest quality."
 
It's a hermetic sealed system. It should not need topping off. If it is low then you need to find and repair the leak. There are no shraders so tubes
need to be cut and valves soldered in. If there is positive charge in the system you first need a detector tool to find the leak. Most likely the
condenser coil bad as that gets most outside abuse. The unit takes so little charge I would go with real R22 as cost is low due to low pounds.
Is cooling poor with compressor running, or is it a thermostat issue shutting off too soon? If so be sure the sensor bulb is not contacting the
evaporator or it will think it is cold in the room and short cycle. If you are successful in actually repairing, you need to pull a vacuum before
recharg.
--
John Lebetski
Woodstock, IL
77 Eleganza II
Source America First
 
Thank you both for your assistance.
Will order a kit when weather gets a little less wet.

--