>All electrical circuits in my 75 PB work fine while connected to shore power.
>But, when connected to and running the Onan, the circuit for the coach
>receptacles and the rear A/C circuit are dead - no voltage. This indicates to
>me that the problem is between the generator and the generator receptacle.
>When I read voltage at the generator receptacle, the right side reads 130
>volts and the left side reads 17 volts. The schematic in the manual shows
>just two wires from the generator to the receptacle but I think there are
>more likely to be four. If one is open or has a poor connection, it might
>explain the voltage problem. The PO replaced the original Onan and in so
>doing, removed the roll out feature. It is therefore difficult to check the
>leads from the generator but it is possible from the inside if a panel is
>removed. I will check the connection at the generator that way and the leads
>to the receptacle, but if they seem OK, could the problem be in the generator
>itself?
>
>Andy M PA
Andy - Jim Walker of Texas was coming through New Mexico in early May
and had a similar problem. He and I attacked the problem in the
local Walmart parking lot. First we thought that it might me a bad
diode set but when I put in a new one still no 120 volt in the coach.
You can check to see if there is 120 volt output by pulling the small
panel off the box with the reset button. This in in the 120 volt
output circuit. You put one lead of your volt meter to ground and
the other lead to the reset switch. You should check both sides of
the reset. If you have 120 volts on both sides then the reset button
is working and so in the generator. If 120 on only one side of the
reset switch and zero on the other side then you have a bad reset
switch or a tripped switch. Push the button to reset it and then
check the other side. You should have 120 volts on both sides. If
you have zero volts on both sides then the problem is in the Onan.
Might be diode, brushes, or something else.
If you have 120 volts on each side then go to the box where your
power cord plugs in. Check to see that you have 120 volts at the
receptacle. If not, then you probably have a problem with the two
wires (only two wires) that lead from the Onan to the receptacle.
From the reset box at the Onan, a wire goes down and out the rear
bottom corner (there are two wires only - a hot lead from the reset
box and a ground lead). From that corner of the Onan box they go
into the wall of the GMC just in front of the lower part of the Onan.
From there they go up to the receptacle that your power cord plugs
into. The power cord goes to your breaker box.
With Jim Walkers GMC we did have voltage at the reset box. We did
NOT have voltage at the receptacle. First we took apart the
receptacle. No voltage on the wires at the back. We then traced the
wires going from the Onan into the wall. We found a two connector
plug in that line near the Onan and found that it was badly corroded.
We cut out the plug and hard wired the wires together and that solved
the problem.
Don't know if this is your problem but you might want to use this
procedure to check things out.
Emery Stora
77 Kingsley
Santa Fe, NM
>But, when connected to and running the Onan, the circuit for the coach
>receptacles and the rear A/C circuit are dead - no voltage. This indicates to
>me that the problem is between the generator and the generator receptacle.
>When I read voltage at the generator receptacle, the right side reads 130
>volts and the left side reads 17 volts. The schematic in the manual shows
>just two wires from the generator to the receptacle but I think there are
>more likely to be four. If one is open or has a poor connection, it might
>explain the voltage problem. The PO replaced the original Onan and in so
>doing, removed the roll out feature. It is therefore difficult to check the
>leads from the generator but it is possible from the inside if a panel is
>removed. I will check the connection at the generator that way and the leads
>to the receptacle, but if they seem OK, could the problem be in the generator
>itself?
>
>Andy M PA
Andy - Jim Walker of Texas was coming through New Mexico in early May
and had a similar problem. He and I attacked the problem in the
local Walmart parking lot. First we thought that it might me a bad
diode set but when I put in a new one still no 120 volt in the coach.
You can check to see if there is 120 volt output by pulling the small
panel off the box with the reset button. This in in the 120 volt
output circuit. You put one lead of your volt meter to ground and
the other lead to the reset switch. You should check both sides of
the reset. If you have 120 volts on both sides then the reset button
is working and so in the generator. If 120 on only one side of the
reset switch and zero on the other side then you have a bad reset
switch or a tripped switch. Push the button to reset it and then
check the other side. You should have 120 volts on both sides. If
you have zero volts on both sides then the problem is in the Onan.
Might be diode, brushes, or something else.
If you have 120 volts on each side then go to the box where your
power cord plugs in. Check to see that you have 120 volts at the
receptacle. If not, then you probably have a problem with the two
wires (only two wires) that lead from the Onan to the receptacle.
From the reset box at the Onan, a wire goes down and out the rear
bottom corner (there are two wires only - a hot lead from the reset
box and a ground lead). From that corner of the Onan box they go
into the wall of the GMC just in front of the lower part of the Onan.
From there they go up to the receptacle that your power cord plugs
into. The power cord goes to your breaker box.
With Jim Walkers GMC we did have voltage at the reset box. We did
NOT have voltage at the receptacle. First we took apart the
receptacle. No voltage on the wires at the back. We then traced the
wires going from the Onan into the wall. We found a two connector
plug in that line near the Onan and found that it was badly corroded.
We cut out the plug and hard wired the wires together and that solved
the problem.
Don't know if this is your problem but you might want to use this
procedure to check things out.
Emery Stora
77 Kingsley
Santa Fe, NM